Skylar One Self-Monitoring
Skylar One includes various tools that enable your Skylar One system to monitor the appliances within your system as well as your other Skylar One stacks. This proactive system health monitoring helps prevent outages and other major issues.
The Workflow for Skylar One Self-Monitoring
The workflow for Skylar One self-monitoring is:
  1. Ensure you have the latest version of the required PowerPacks.
  2. Create the appropriate credentials.
  3. Enable connectivity on port 7707 (not required in all scenarios)
  4. Discover your Skylar One devices.
  5. Align additional Dynamic Applications to your Skylar One devices using device templates.
  6. Ensure the correct credentials are aligned to the Dynamic Applications.
  7. Configure run book automations to populate dashboards with data about your Skylar One devices.
PowerPacks Used for Self-Monitoring
To self-monitor Skylar One, you must first have the latest versions of the following PowerPacks:
Skylar One: Operational Insights PowerPacks
To self-monitor Skylar One, you will need to download on of the following "Skylar One: Operational Insights" PowerPacks, depending on your system configuration:
  • "Skylar One: Operational Insights - On-Premises" is required for MariaDB databases.
  • "Skylar One: Operational Insights - SaaS" is required for Aurora RDS databases or SaaS stacks.
These PowerPacks include a variety of Dynamic Applications, run book actions and automation policies, dashboards, and other tools that provide additional Skylar One platform health visibility.
For a Skylar One Software-as-a-Service (SaaS) deployment, the "Skylar One: Operational Insights - SaaS" PowerPack is the only supported method for monitoring your SaaS stacks. For more information about SaaS, see SaaS and On-prem Deployments of Skylar One.
Starting with version 106.3 of the "Skylar One: Operational Insights - SaaS" PowerPack, you no longer need a dedicated Self-monitoring Collector (SMC). Version 106.3 also includes the following features:
  • You can deploy the "Operational Insights" directly on one of your existing collectors, with no additional SMC component needed. You can continue to monitor your environment as before; removing the SMC requirement does not reduce or limit your monitoring capabilities.
  • You regain the ability to upgrade the "Operational Insights" PowerPack directly through your standard PowerPack upgrade process, without needing to make changes to the SMC.
The "Skylar One: Operational Insights" PowerPacks are not included by default in Skylar One releases. To use them, you must first download them from the ScienceLogic Support site and then install them on your Skylar One system. If you are on a SaaS deployment, you will need to open a Service Request case with the ScienceLogic SRE team to get the "Skylar One: Operational Insights - SaaS" PowerPack.
You should periodically check the ScienceLogic Support Site at https://support.sciencelogic.com/s/skylar-one/powerpacks for any newer versions of the "Skylar One: Operational Insights - On-Premise" or "Skylar One: Operational Insights - SaaS" PowerPacks.
If you are downloading version 105 or later of the "Skylar One: Operational Insights - On-Premise" or "Skylar One: Operational Insights - SaaS" PowerPack, then you can follow the steps below to download and install the PowerPack directly.
However, if you are upgrading from version 104 or earlier, there are additional steps that you must follow. These steps are detailed in the user manual that can be downloaded along with the PowerPack file on the ScienceLogic Support Center at https://support.sciencelogic.com/s/skylar-one/powerpacks.
ScienceLogic Support Pack
This PowerPack is no longer relevant for Skylar One Software-as-a-Service (SaaS) deployments.
Skylar One includes the "ScienceLogic Support Pack" PowerPack by default with all Skylar One releases.
This PowerPack was developed by ScienceLogic Support to help you monitor your Skylar One systems. It allows a Skylar One stack to monitor itself and other Skylar One stacks.
The "ScienceLogic Support Pack" PowerPack:
  • ensures that all Skylar One appliances are monitored and running the same version of Skylar One
  • ensures that all Skylar One appliances appear on the Devices page
  • ensures that configuration files on Skylar One appliances and clusters are kept in sync
  • monitors the health and configuration of MariaDB
  • generates alerts when system resources like disk-space are approaching capacity
  • monitors DNS entries for Database Servers and All-In-One Appliances
  • monitors long-running processes and queries
  • monitors out-of-memory conditions
  • monitors storage features, including ZSWAP, ZRAM, and LVM Thin Pools, with alerting for resource contention and high usage
  • collects Non-Uniform Memory Access (NUMA) information and statistics
  • collects pressure stall information
  • ensures that CRM and corosync configurations are up to date
  • ensures that configuration files match among high-availability Database Servers
  • monitors crucial Skylar One processes like data pull and config_push
  • monitors "rows behind" situations and generates alerts
  • monitors and fixes backlogs of email messages
  • generates alerts if any of the following files differ:
    • /etc/silo.conf
    • /etc/siteconfig/mysql.siteconfig
    • /etc/siteconfig/siloconf.siteconfig
  • collects telemetry related to Device Groups
The Dynamic Applications included in the PowerPack should automatically align when you discover your Skylar One appliances for self-monitoring.
For more information about the Dynamic Applications that are included in the "ScienceLogic Support Pack" PowerPack, see the following knowledge base article: https://support.sciencelogic.com/s/article/2951.
Data Pull Support
The "Data Pull Support" PowerPack is also included by default in all Skylar One releases.
It includes several Dynamic Applications that use SNMP to collect configuration and performance data related to data pull, which is the process by which Skylar One Database Servers retrieve collected data from Data Collectors and Message Collectors.
Because the PowerPack is included in Skylar One installations and upgrades by default, you cannot download it from the ScienceLogic Support site. Whenever you upgrade your Skylar One stack to the latest release, you should go to the PowerPack Manager page (System > Manage > PowerPacks) to check for a new version of the "Data Pull Support" PowerPack. For more information about updating default PowerPacks, see the section on How Skylar One Updates Default PowerPacks.
Credentials Required for Self-Monitoring
For more background on using credentials in Skylar One, see the section on Credentials.
To self-monitor Skylar One, you must create a minimum of three credentials:
Your Skylar One system includes default example credentials for each of these credential types. However, ScienceLogic does not recommend that you use or edit the example credentials. Instead, you should create new credentials specific to your system.
Creating an SNMP Credential for Self-Monitoring
Prior to creating the SNMP credential for Skylar One self-monitoring, you must configure the SNMP settings for your Skylar One appliances, including providing access to SNMPD for those appliances. To do this, you must be familiar with your company's policies on SNMP and the required SNMP settings.
Newly installed Skylar One systems are configured with default settings that allow read-only access for SNMPD and enable you to align the default example SNMP credentials that are included in Skylar One. ScienceLogic strongly recommends that you configure SNMPD access with community/user access for your Skylar One environment and do not use the default example SNMP credentials.
The following procedure is the only supported way of customizing the SNMPD configuration on a Skylar One system. Other SNMPD customizations might get overwritten without warning.
To configure SNMP for your Skylar One appliances:
  1. Open an SSH session on the Skylar One appliance using either the sl1user account or the em7admin account.
    ScienceLogic recommends using the sl1user account, as this account has fewer privileges and is designed for basic system setup tasks. If you are unfamiliar with this account, see the Role-based sl1user Account section.
    If you opt to use the em7admin account, you must run the following command to bring up the menu:
    sudo /usr/local/bin/slmenu
  2. From the menu, select the SNMP Configuration option and then press Enter.
  3. The SNMP Configuration menu displays your current SNMP settings, as well as options to change the SNMPv2 Community or SNMPv3 settings. After reviewing your current settings, do one of the following:
    • To change the SNMPv2 community string, use the arrow keys on your keyboard to navigate to that option on the menu and then press Enter. Proceed to step 4.
    • To change the SNMPv3 settings, use the arrow keys on your keyboard to navigate to that option on the menu and then press Enter. Proceed to step 5.
    You can use the following special characters in the SNMPv2 community string and SNMPv3 settings:
    + _ ) ( * & ^ % $ # @ ! | } { " : ? > < = - \ ] [ ; / . ,
  4. In the Change SNMPv2 Community menu, enter a new community string that you want to use for SNMPv1/2 access in Skylar One. Alternatively, you can disable SNMPv1/2 access by deleting the string and leaving the field blank. When you are done, navigate to OK and press Enter. If you want to also change your SNMPv3 settings, proceed to step 5; otherwise, to leave your SNMPv3 settings as they are, proceed to step 6 to return to the SNMP Configuration menu.
  5. In the Change SNMPv3 Settings menu, use the arrow keys on your keyboard to navigate to the following fields and update their values as needed for your configuration:
    • SNMPv3 User. Enter the username you want to use for SNMPv3 authentication.
    • SNMPv3 Auth Password. Enter the password you want to use to authenticate the SNMPv3 user. This password must contain at least 8 characters.
    • SNMPv3 Auth Password (confirm). Re-enter the authentication password for the SNMPv3 user.
    • SNMPv3 Auth Protocol. Enter the authentication protocol for the SNMPv3 user, based on your company policies. The possible values for this field appear on the Change SNMPv3 Settings menu.
    • SNMPv3 Privacy Password. Enter the password you want to use to ensure data privacy for the SNMPv3 user.
    • SNMPv3 Privacy Password (confirm). Re-enter the privacy password.
    • SNMPv3 Privacy Protocol. Enter the data privacy protocol used for data encryption and decryption, based on your company policies. The possible values for this field appear on the Change SNMPv3 Settings menu.
    When you are done changing your SNMPv3 settings, navigate to OK and press Enter to return to the SNMP Configuration menu.
  6. On the SNMP Configuration menu, review the updated SNMP settings. Repeat steps 3-5 as necessary to make any additional changes. To save the new settings, navigate to the Save option and press Enter.
  7. On the Save Settings Confirmation menu, to confirm your new settings, navigate to the Yes option and press Enter.
  8. Repeat these steps for all Skylar One appliances.
After you have configured your SNMP settings, you can create one or more SNMP credentials for Skylar One self-monitoring. To do so, follow the steps in the section on Defining an SNMP Credential. Use the values you configured in the previous section when creating your SNMP credentials.
Creating Database Credentials for Self-Monitoring
For Skylar One self-monitoring, you will need at least two database credentials:
  • One database credential for your Database Server
  • One or more database credentials for your Data Collectors and Message Collectors
If you have a Skylar One SaaS deployment, the RDS credential will be created for you. If it is not or you are unsure which one it is, contact ScienceLogic Support.
If your Data Collectors and Message Collectors all use the same database user and password, then you can use a single credential for all of them. If they use unique database users and passwords, then you will need to create credentials for each Data Collector or Message Collector.
To create the database credentials, follow the steps in the section on Defining a Database Credential. When doing so, use the following guidance for completing these fields:
  • Timeout (ms). Enter "0".
  • Database Type. Select MySQL.
  • Database Name. Enter "master".
  • Database User. Typically, this value will either be "clientdbuser" or "root". If you are unsure of which value to use, refer to your silo.conf file for your system.
  • Database Password. Enter the password you have set for the database.
  • Hostname/IP. Enter "%D".
  • Port. For your Database Server or Aurora RDS credential, enter "7706". For your Data Collector and Message Collector credentials, enter "7707".
Enabling Connectivity on Port 7707
On-premises Data Collector and Message Collector appliances do not allow connections to port 7707 (MariaDB) from an external device. Therefore, if you want one on-premises Data Collector to monitor another Data Collector or Message Collector, then there are some additional steps you must take to enable connectivity on port 7707.
Some Dynamic Applications collect data from MariaDB/ Aurora and should be able to connect to port 7706 (DB/AIO) or 7707 (Data/ Message Collector) Please ensure that any firewalls between the monitoring collector and the monitored appliances allow communication from the monitoring collector to the monitored appliances on port 7706 or 7707.
If this scenario does not apply to your Skylar One configuration, then you can skip this section.
For the instructions below, consider the following scenario:
  • "Collector A" is the Data Collector or Message Collector you want to monitor.
  • "Collector B" is the Data Collector on which you want to monitor Collector A.
To enable connectivity on port 7707 in this scenario:
  1. Log in to the Web Configuration Utility for Collector A using any web browser supported by Skylar One. The address of the Web Configuration Utility is in the following format:
    https://<Collector-A-IP-address>:7700
    For AWS instances, Collector-A-IP-address is the public IP for the AWS instance for Collector A. To locate the public IP address for an AWS instance, go to AWS, go to the Instances page, and highlight an instance. The Description tab in the lower pane will display the public IP.
  2. When prompted to enter your username and password, log in as the "em7admin" user with the appropriate password. After logging in, the main Configuration Utility page appears.
  3. Click the Device Settings button. The Settings page appears.
  4. On the Settings page, add the IP address for Collector B to the Database IP Address field, immediately after the IP address that is already listed for Collector A, separated by a comma and no space. For example, if the IP address for Collector A is 10.10.10.1 and the IP address for Collector B is 10.20.20.2, then you would enter "10.10.10.1,10.20.20.2" (without the quotation marks) in the Database IP Address field.
  5. Click Save and log out of the Web Configuration Utility. With this change saved, the firewalld rules on Collector A will be updated to allow connectivity to port 7706 (MariaDB) from the IP address for Collector B.
Discovering Your Skylar One Devices
After creating your credentials, you will then use those credentials to discover your Skylar One appliances.
To do so, follow the instructions found in the section Adding Devices Using Unguided Discovery.
While configuring your discovery policy, make sure to do the following:
  • Select the SNMP credential you created.
  • Additionally, select one or more of the database credentials you created, depending on whether you are discovering the Database Server, one or more Data Collectors or Message Collectors, or both the Database Server and one or more collectors.
  • When listing the IP addresses that you want to discover, include the IP addresses of all Skylar One appliances that you want to discover.
  • Under Advanced Options, make sure the Discover non-SNMP toggle is turned off.
Upon discovering your Skylar One appliances, most SNMP-based Dynamic Applications should automatically be aligned to the appropriate devices.
After discovering your Skylar One appliances, you can go to the Appliance Manager page (System > Settings > Appliances) to confirm that they all appear on the page and that their settings are correct. For example, the Device Name on the Devices and Device Manager (Devices > Classic Devices, or Registry > Devices > Device Manager in the classic user interface) pages should match the Device Name on the Appliance Manager page.
Aligning Skylar One Self-Monitoring Dynamic Applications
After discovering your Skylar One appliances, you must ensure that they are properly set up for monitoring. The easiest way to do this is to apply the device templates that are included in the "ScienceLogic Support Pack," "Data Pull Support," and "Skylar One: Operational Insights" PowerPacks to ensure your Skylar One device classes have the necessary Dynamic Applications aligned to them.
To align the appropriate self-monitoring Dynamic Applications using device templates:
  2. In the Device Class column, use the filter field to search for the appropriate device class based on the table at the end of this section.
  3. Select the checkbox for each row that contains the device class type that you want to modify.
    Because each of these device classes requires a different configuration, you should modify devices of only one device class at a time.
  4. From the Select Action field at the bottom of the page, select MODIFY by Template and then click Go. The Bulk Device Configuration modal appears.
  5. In the Template drop-down field at the top of the Bulk Device Configuration modal, select the appropriate device template based on the table at the bottom of this section.
    You can select only one device template at a time. For device classes that have multiple device templates, complete steps 5-7 for one template, then repeat the steps for the other templates.
  6. Click the Dyn Apps tab and verify that a list of Dynamic Applications appear in the Subtemplate Selection pane.
  7. Click Apply, and then click Confirm.
  8. Repeat steps 1-7 as needed until all of the device classes needed for self-monitoring have all of the appropriate device templates applied to them, based on the following table:
Appliance Type Device Class Device Templates
Primary Database Server or cluster IP device
Skylar One Database
Support: Skylar One Active DB/VIP
Skylar One: Database - On Premise
Skylar One System Processes
Administration Portal
Skylar One Admin Portal
Support: Skylar One Application Portal
Data Collector
Skylar One Data Collector
Support: Skylar One Collector
Skylar One: Collectors
Message Collector
Skylar One Message Collector
Support: Skylar One Message Collector
It can take Dynamic Applications up to 15 minutes to start collecting data after they are aligned.
Aligning the Correct Credentials to Your Devices
When you align the self-monitoring Dynamic Applications to your Skylar One appliances using the device templates that are included in the self-monitoring PowerPacks, those Dynamic Applications use the unedited versions of the "Skylar One CDB" and "Skylar One Collector Database" credentials that are included in the PowerPacks.
Now, you must edit those Dynamic Applications to use the copies you made for those credentials instead of the original versions that are included in the self-monitoring PowerPacks. This will prevent Skylar One from overwriting your self-monitoring configuration whenever you install updates for those PowerPacks in the future.
To ensure the correct credentials are aligned to your Skylar One devices:
  2. Locate one of your Skylar One devices and click its wrench icon (wrench icon). The Device Administration panel appears.
  3. On the Device Administration panel, click the Collections tab. The Dynamic Application Collections page appears.
  4. On the Dynamic Application Collections page, locate and select the checkboxes for any Dynamic Applications that have "Skylar One CDB" listed in the Credential column.
  5. From the Select Action field at the bottom of the page, select the database credential you created for the Database Server or Aurora RDS from the list and then click Go. The Dynamic Application Collections page will refresh and the database credential you created should now be listed in the Credential column for the Dynamic Applications you selected.
  6. Repeat steps 4 and 5 to replace the credential for any Dynamic Applications that currently have the "Skylar One Collector Database" credential in the Credential column with the database credential you created for Data Collectors and Message Collectors.
Configuring Run Book Automations to Populate Dashboards
The "Skylar One: Operational Insights" PowerPacks include two run book actions and automation policies: "Skylar One: Collector Data Collection" and "Skylar One: System Log Data Collection."
These automations collect data that is then used to populate the "Collector Performance" and "System Logs Summary" dashboards, respectively, with data relating to your monitored Skylar One appliances.
If you are using the ScienceLogic Skylar One Operational Insights - On-Premise Community PowerPack, please review the manual that is shipped with the PowerPack for more information on configuring run book automations. Be advised, the manual shipped with the PowerPack is not official ScienceLogic documentation.
The "Skylar One: Collector Data Collection" automation is responsible for collecting Skylar One Collector-specific data that is used in the "Collector Performance" dashboard. The automation policy is configured to trigger the "Skylar One: Collector Data Collection" run book action four times once per hour. The automation helps identify Skylar One Collectors that have been discovered and match the following criteria required to appear in the "Collector Performance" dashboard:
  • Data Collectors and Message Collectors should be discovered as managed devices.
  • The discovered Skylar One Collector's Device Name on the Devices and Device Manager (Devices > Classic Devices, or Registry > Devices > Device Manager in the classic user interface) pages should match the name of the same collector from the Appliance Manager page (System > Settings > Appliances).
  • The Skylar One Collectors should have the following two Dynamic Applications aligned and successfully collecting data:
    • Support: File System
    • Host Resource: Configuration
  • The Data Collectors should be in a collector group (CUG). This does not apply to Message Collectors.
When the automation runs, it stores the data in a custom table, which is then read and displayed by the dashboard widget.
The "Skylar One: System Log Data Collection" automation is responsible for collecting system log-specific data that is used in the "System Logs Summary" dashboard. The Automation is configured to trigger the "Skylar One: System Log Data Collection" run book action five times once per hour.
The automation parses the top problem logs, including SIGTERMs, PoolWorker logs, and unhandled exceptions.
If the total system log count is greater than 6 million, the automation will not collect data; instead, the "System Logs Summary" dashboard will display a message stating that the log count is too high. If this occurs, delete older logs to bring the total count below 6 million.
Verifying Your Devices
Before you configure the run book automation policies required to populate the "Collector Performance" and "System Logs Summary" dashboards, you must verify that you have the necessary devices in your Skylar One system. The method for doing so will vary based on whether you have an on-premises Skylar One system or a SaaS Skylar One system. Both methods are described below.
On-Premises Skylar One Systems
To verify that you have the necessary devices:
  2. In the Device Class column, use the filter field to search for devices with the "Skylar One Database" device class.
  3. Verify that all Database Servers are discovered.
  4. If the Database Servers are not discovered, then you must discover them. Otherwise, if they are, you can skip to the next section.
SaaS Skylar One Systems
To verify that you have the necessary device:
  2. In the Device Name column, use the filter field to search for a device with the name "Skylar One Stats".
  3. Verify that the "Skylar One Stats" device exists. If it does not yet exist, proceed to the next step. Otherwise, if it does, you can skip to the next section.
  4. From the Actions menu, select Create Virtual Device. The Create Virtual Device modal appears.
    • Device Name. Type "Skylar One Stats".
    • Organization. Select System.
    • Device Class. Select Virtual Device | Dynamic App Emissary.
    • Collector. Select Self Monitoring Collector.
  6. Click Add and then exit the modal.
Configuring the Run Book Automations
To configure the run book automation policies required to populate the "Collector Performance" and "System Logs Summary" dashboards:
  2. In the Automation Policy Name column, use the filter field to search for a policy with the name "Skylar One: Collector Data Collection".
  3. Click the wrench icon (wrench icon) for the "Skylar One: Collector Data Collection" automation policy. The Automation Policy Editor modal appears.
  4. In the Available Devices field, use the filter field to search for the appropriate device:
    • For on-premises Skylar One deployments, search for the active Skylar One Database Server device.
    • For SaaS Skylar One deployments, search for the "Skylar One Stats" device.
  5. Select the device from the Available Devices field and then click the right arrow icon to move it to the Aligned Devices field.
  6. Click Save and then exit the Automation Policy Editor modal.
  7. Repeat steps 1-6 to search for and configure the "Skylar One" System Log Data Collection" automation policy.
Additional Self-Monitoring Resources
For information about additional steps you can take in Skylar One to monitor your Skylar One system, see the following sections: