Responding to Events

Download this manual as a PDF file

This section describes the different ways in which you can respond to events in Skylar One.

Responding to Events

When events occur, there are multiple ways you can respond to them:

  • Acknowledge. Lets other users know that you are aware of an event and are working on a response.
  • Add a Note. Adds additional text to an event. Notes can be displayed on the Events page and can be included in automation actions.
  • Clear. Removes an instance of an event from the Events page. The cleared instance is no longer displayed.
  • Suppress. Specifies that if the event occurs again on the same device, the event is not displayed on the Events page.
  • Disable. Specifies that if the event occurs on any device or is triggered by any application or policy, the event does not appear in the Event Console.

Selecting Multiple Events

On the Events page, you can use the checkboxes to the left of the event to select more than one event at a time. After you select the events, you can click the Acknowledge or Clear button at the bottom of the page to acknowledge or clear those events simultaneously.

If you do not want to acknowledge or clear the selected events, click the Deselect All button to deselect the checkboxes.

If you want to select all of the events that are currently showing on the tab, click the Select All Visible button.

Acknowledging and Clearing Events

When you acknowledge an event, you let other users know that you are aware of that event and that you are working on a response. 

When you clear an event, you let other users know that this event has been addressed. Clearing an event removes a single instance of the event from the Events page. If the event occurs again on the same device, it reappears on the Events page and on the Events tab of the Device Investigator page, even if you previously cleared that event.

When you acknowledge a parent event, all masked events under that parent event are also acknowledged.

To acknowledge and clear events:

  1. To acknowledge an event, find the event on the Events page and click the Acknowledge button for that event. Your user name replaces the Acknowledge button for that event.

You can also click the Acknowledge button in a specific event's Investigator page.

  1. To see when an event was acknowledged and who acknowledged it, hover your mouse over an acknowledged field.
  2. If an event was acknowledged by another user and you have the relevant permissions, you can click the Reacknowledge button to acknowledge that event.
  3. To clear an event, click the Clear button. The event is removed from the Events page.

If you want to hide the Acknowledge or Clear buttons on the Events page, click the gear icon (Image of the gear icon) and deselect those columns.

Viewing and Editing Event Notes

From the Events page, you can access event notes, which contain event definitions, probable causes, and resolutions for the event, along with a text field where you can add more information about the event or the device you are monitoring. If event notes already exist for that event, the opening text of that note appears in the Event Note column of the Events page.

To view or edit an event note:

  1. On the Events page, click the note icon (note icon) for that event. The Edit Event Note modal appears.

    You can also edit an event note on the Events page by clicking the actions icon (actions icon) for that event and selecting Edit Event Note. This is helpful if you have hidden the Event Note column on the Events page. To add or edit an event note for multiple events, check the box next to the events for which you want to edit the note, then click the Edit Note button at the top of the inventory table.

  1. Type your additional text for the event note and then click Save. The event note is updated.

Viewing the Event Policy

From the Events page, you can view the event policy for an event, which allows you to view a description of the policy, enable or disable the policy, and edit policy details.

To view an event policy from the Events page:

  1. On the Events page, click the actions icon (actions icon) for that event and select View Event Policy. The Event Policy Editor page appears for that event:

    The Event Policy Editor page

  1. Click the Edit button to edit the Event Policy. For more information, see Defining and Editing Event Policies.

Suppressing and Unsuppressing an Event for a Device

When you suppress an event, you are specifying that in the future, if this event occurs again on the same device, the event does not appear in the Events page or the Events tab for a device.

If a suppressed event occurs on a different device, it appears in the Events page and on the Events tab for that different device.

When you suppress an event, the current instance of the event still appears in the Events. To remove the current instance from the event console, clear the event. (For more information, see the section Clearing One or More Events.)

To suppress an event, non-administrator users must be granted one or more access keys that include the following access hooks: Events/Event:View and Event:Clear. Non-administrator users can then view and suppress events that belong to the same organization(s) as the user. For more information on access hooks, see the section on Access Permissions.

Suppressing an Event for a Single Device

To suppress an event:

  1. Go to the Events page.
  2. Click the actions icon (actions icon) for the event you want to suppress and select Suppress Event for this Device. In the future, if this event occurs again on the same device, the event does not appear in the Events page. Additionally, the suppressed event displays on the Event Suppressions page (Events > Event Suppressions).

Non-administrator user accounts can only view suppressed events that are aligned with the same organization(s) to which the user is aligned. Administrator users can view all suppressed events.

Suppressing an Event on Multiple Devices

When you suppress an event on multiple devices, you are specifying that, in the future, if this event occurs again on any of those devices, the event does not appear in the Events page or in the Viewing Events page for any of those devices.

To suppress an event on multiple devices:

  1. Go to the Event Policies page (Events > Event Policies, or Registry > Events > Event Manager in the classic user interface).
  2. In the Event Policies page, click the actions icon (actions icon) of the event policy you want to edit and select Edit.
  3. The selected event policy is displayed in the Event Policy Editor page, where you can edit one or more properties of the event policy.
  1. Click the Basic tab.
  2. On the Basic tab, click the Configure Suppressions button. The Select Suppressions modal appears. From the Select Suppressions modal, you can select the devices or device groups on which to suppress the event. To do so:
  • Click Devices to select one or more devices on which to suppress the event. When you click Devices, the available devices appear below. Select the checkboxes of the devices you want to add to the suppression list.
  • Click Device Groups to select one or more device groups on which to suppress the event. When you click Device Groups, the available devices appear below. Select the checkboxes of the device groups you want to add to the suppression list.
  1. Click Save.

Unsuppressing an Event for a Single Device

On the Event Suppressions page (Events > Event Suppressions), you can view a list of all suppressed events in Skylar One and choose to unsuppress one or more of those events. When you unsuppress an event, if this event occurs again on the same device, the event appears in the Events page.

To unsuppress an event, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Registry, Registry>Events>Suppressions, and Event:Suppressions. Non-administrator user accounts can then view a list of suppressed events that belong to the same organization as the user. Non-administrator user accounts can also unsuppress one or more of these suppressed events. For more information on access hooks, see the section on Access Permissions.

To unsuppress an event:

  1. Go to the Event Suppressions page (Events > Event Suppressions).
  2. Select the checkbox for each event you want to unsuppress.
  3. Click the Delete button that appears in the top left.

Unsuppressing All Instances of an Event

You can simultaneously unsuppress all instances of an event. That is, if a single event has been suppressed for multiple devices, you can unsuppress the event on all devices. In the future, if the unsuppressed event occurs again on any device, the event appears in the Events page.

To unsuppress an event on all devices, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Registry, Registry>Events>Event Manager, and Event:Add/Rem. Non-administrator user accounts can then access the Event Policies page and unsuppress one or more events on all devices. For more information on access hooks, see the section on Access Permissions.

To unsuppress an event on all devices:

  1. Go to the Event Policies page (Events > Event Policies, or Registry > Events > Event Manager in the classic user interface).
  2. Select the checkbox for the event you want to unsuppress on all devices.
  3. Click Clear Suppressions. In the future, if the unsuppressed event occurs again on any device, it appears in the Events page or in the Viewing Events page for the device.

Viewing Suppressed Events

From the Event Suppressions page (Events > Event Suppressions), you can view a list of all suppressed events in Skylar One.

The Event Suppressions page displays the following about each suppressed event:

  • Device/Group Name. The name of the device or device group associated with the suppressed event.

  • IP Address. The IP address of the device or device group associated with the suppressed event.

  • Event Policy ID. Unique numeric ID for the event policy associated with the suppressed event.

  • Event Policy Name. The name of the event policy associated with the suppressed event.

  • Severity. The severity of the event. For more information about severity values, see the section Understanding Event Severity.

  • Created Date. Date and time when the event was suppressed.

  • Created By. The user ID of the user who suppressed the event.

You can sort the list by a column's values by clicking its column heading. You can also filter the items on the page by typing or selecting filter options in one or more of the filters found above the columns. For more information, see the topic on Filtering Inventory Pages.

You can adjust the size of the rows and the size of the row text on this inventory page. For more information, see the topic on Adjusting the Row Density.

You can rearrange the columns in the list by clicking and dragging the column to a new location. You can adjust a column's width by clicking and dragging the right edge of the column. For more information on editing and adding columns, see the topic on Editing the Settings for an Inventory Page.

Enabling and Disabling Events

You can simultaneously disable one or more events on all devices. When an event is disabled, it no longer appears in the Events page for any devices. You can also enable an event that has been disabled.

To disable or enable an event on all devices, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Registry, Registry>Events>Event Manager, and Event:Add/Rem. Non-administrator user accounts can then access the Event Policies page and enable one or more events on all devices. For more information on access hooks, see the section on Access Permissions.

Disabling Events

To disable one or more events:

  1. Go to the Event Policies page (Events > Event Policies, or Registry > Events > Event Manager in the classic user interface).
  2. Select the checkboxes for the events you want to disable.
  3. Click Disable. The selected events no longer appear in Skylar One for any device, application, or policy.

Enabling Events

To enable one or more events:

  1. Go to the Event Policies page (Events > Event Policies, or Registry > Events > Event Manager in the classic user interface).
  2. Select the checkboxes for the events you want to enable.
  3. Click Enable. The selected event(s) once again appear in Skylar One.

Creating a Ticket from an Event

On the Events page, you can create a ticket from an event by clicking the actions icon (actions icon) for that event and selecting Create Ticket. The Ticket Editor appears. For more information about creating a ticket from the Events page, see the Creating a Ticket from the List of Events section.

Responding to Events in the Classic Event Console

On the Event Console page (Events > Classic Events, or the Events tab in the classic user interface), you can acknowledge new events as they are detected by the system. Acknowledging an event lets other users know that you are aware of the event and working to resolve it.

When an event has been acknowledged, the acknowledging user's name appears in the Acknowledged column. This lets other users know that someone is investigating or taking action on the event.

To acknowledge an event, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Events/Event:View and Event:Acknowledge. Non-administrator user accounts can then view and acknowledge events in the same organization(s) as the user. For more information on Access Keys, see the section on Access Permissions.

When you acknowledge a parent event, all masked events under that parent event are also acknowledged. For more information about parent/child events and masked events, see the section on Event Correlation and Parent and Child Events.

To acknowledge a single event:

  1. Go to the Events tab in the classic user interface.
  2. In the Event Console page, find the event you want to acknowledge and click on the checkbox in the Acknowledged column for that event.
  3. A check mark and your username appear in the Acknowledged column for that event.
  4. You can also acknowledge an event that has already been acknowledged by another user. To do this, click on the check mark icon. Your username now appears in the Acknowledged column for that event, replacing the username of the person who previously acknowledged the event.

To acknowledge multiple events:

  1. In the Event Console page, select the checkbox in the far right column for each event that you want to acknowledge.

  1. Acknowledge the event(s) by doing one of the following:
  • Click the Ack button.
  • From the Select Action drop-down list, select Acknowledge, then click the Go button.
  1. For each acknowledged event, a check mark  and your username appear in the Acknowledged column.

NOTE: Users cannot unacknowledge an event. Another person can acknowledge the event to change the name associated with the acknowledged event, but you cannot remove an acknowledgment.

Adding a Note About an Event in the Classic Event Console

You can add brief notes to an event in the Event Console page. Each note appears in the Note column for an event. Skylar One does not keep a historical record of each note.

NOTE: A note can be included in an action policy by using the %_user_note variable. For details on creating automation policies and action policies, see the sections on automation policies and action policies.

To create or edit a note for an event:

  1. In the Event Console page, find the event to which you want to add a note.
  2. In the Note column for that event, click on the wrench icon (wrench icon).
  3. In the Add a Note modal, enter the note text. Click Save to save the note.
  4. The new or edited text appears in the Note column for the event.

Adding a Note to Multiple Events in the Classic Event Console

You can add a brief note to multiple events simultaneously and/or overwrite existing notes for multiple events. The note appears in the Note column for each event and in the Note field in the Event Information page for each event. Skylar One does not keep a historical record of each note.

NOTE: A note can be included in an action policy by using the %_user_note variable. For details on creating automation policies and action policies, see the sections on automation policies and action policies.

To create or edit a note for multiple events:

  1. In the Event Console page, find the events for which you want to add a note and/or overwrite the existing note.
  2. For each event that you want to add and/or edit a note, select the checkbox in the last column.
  3. In the Select Action drop-down field, select Add/Update Event Note, then click the Go button.
  4. In the Add a Note modal, enter the text for the note. Click the Save button.
  5. The new or edited text appears in the Note column for each selected event.

Clearing One or More Events in the Classic Event Console

When you clear an event, you remove only a single instance of the event from the current display in the Event Console page. If the event occurs again on the same entity, it reappears in the Event Console page.

To clear an event, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Events/Event:View and Event:Clear. Non-administrator user accounts can then view and clear events in the same organization(s) as the user. For more information on access hooks, see the section on Access Permissions.

To clear an event:

  1. Go to the Events tab.
  2. In the Event Console page, select the checkbox for each event you want to clear. To select all events in an organization, click the checkmark icon above each organization's group of events.
  1. Clear the event(s) by doing one of the following:
  • Click the Del button.
  • In the Select Action drop-down list, select Clear, then click the Go button.
  1. When you successfully clear an event, it no longer appears in the Event Console page.

The Event Clearing Mode option in the Behavior Settings page (System > Settings > Behavior) affects how rolled-up events and suppressed events can be cleared. For details, see the section on System Settings that Affect Events.

Suppressing an Event on a Single Device in the Classic User Interface

When you suppress an event in the classic Skylar One user interface, you are specifying that in the future, if this event occurs again on the same device, the event does not appear in the Event Console page or the Viewing Events page for a device.

If a suppressed event occurs on a different device, it appears in the Event Console page and on the Viewing Events page for that different device.

When you suppress an event, the current instance of the event still appears in the Event Console. To remove the current instance from the event console, clear the event (see the section Clearing One or More Events).

To suppress an event, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Events/Event:View and Event:Clear. Non-administrator user accounts can then view and suppress events that belong to the same organization(s) as the user. For more information on access hooks, see the section on Access Permissions.

To suppress an event in the classic Skylar One user interface:

  1. Go to the Events tab.
  2. In the Event Console, click the information icon (information icon) for the event you want to suppress.
  3. In the Event Information page, click the Actions menu and select Suppress Event for this Device.
  4. In the future, if this event occurs again on the same device, the event does not appear in the Event Console page.

NOTE: Non-administrator user accounts can view only suppressed events that are aligned with the same organization(s) to which the user is aligned. Administrator users can view all suppressed events.

Suppressing an Event On Multiple Devices in the Classic User Interface

When you suppress an event on multiple devices, you are specifying that, in the future, if this event occurs again on any of those devices, the event does not appear in the Event Console page or in the Viewing Events page for any of those devices.

To suppress an event on multiple devices in the classic Skylar One user interface:

  1. Go to the Event Policy Manager page (Registry > Events > Event Manager).

  2. In the Event Policy Manager page, select the page icon (page icon) of the event you want to suppress.

  3. The Event Policy Editor page appears, with the Suppressions tab selected.

  4. In the Suppressions tab, you can select the devices or device groups on which to suppress the event. To do so:

  • Select one or more device groups in the Available Device Groups field and then click the right arrow button (>>) so those groups appear in the Suppressed Device Groups field.
  • Select one or more devices in the Available Devices field and then click the right arrow button (>>) so those devices appear in the Suppressed Devices field.
  1. Click Save. In the future, if the event occurs on one of the selected devices, the event does not appear in the Event Console page or in the Viewing Events page for the device. The suppressed event appears in the Event Suppression List page (Registry > Events > Suppressions).

Unsuppressing an Event in the Classic User Interface

You can view a list of all suppressed events in Skylar One and choose to unsuppress one or more of those events. When you unsuppress an event, if this event occurs again on the same device, the event appears in the Events page (or the Event Console page in the classic Skylar One user interface) .

To unsuppress an event, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Registry, Registry>Events>Suppressions, and Event:Suppressions. Non-administrator user accounts can then view a list of suppressed events that belong to the same organization as the user. Non-administrator user accounts can also unsuppress one or more of these suppressed events. For more information on access hooks, see the section on Access Permissions.

To unsuppress an event:

  1. Go to the Event Suppression List page (Registry > Events > Suppressions).
  2. In the Event Suppression List page, select the checkbox for each event you want to unsuppress.
  3. In the Select Action drop-down menu, in the lower right, select DELETE Suppression.
  4. Click the Go button.
  5. In the future, if the unsuppressed event occurs again on the same device, the event appears in the Events page (or the Event Console page in the classic Skylar One user interface) .

Unsuppressing All Instances of an Event in the Classic User Interface

You can simultaneously unsuppress all instances of an event. That is, if a single event has been suppressed for multiple devices, you can unsuppress the event on all devices. In the future, if the unsuppressed event occurs again on any device, the event appears in the Event Console page.

To unsuppress an event on all devices, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Registry, Registry>Events>Event Manager, and Event:Add/Rem. Non-administrator user accounts can then access the Event Policy Manager page and unsuppress one or more events on all devices. For more information on access hooks, see the section on Access Permissions.

To unsuppress an event on all devices in the classic Skylar One user interface:

  1. Go to the Event Policy Manager page (Registry > Events > Event Manager).
  2. In the Event Policy Manager page, select the checkbox for the event you want to unsuppress on all devices.
  3. In the Select Action drop-down menu, select CLEAR the Suppression List.
  4. Click the Go button. In the future, if the unsuppressed event occurs again on any device, it appears in the Event Console page or in the Viewing Events page for the device.

Disabling an Event in the Classic User Interface

You can simultaneously disable one or more events on all devices. When an event is disabled, it no longer appears in the Event Console for any devices.

To disable an event on all devices, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Registry, Registry>Events>Event Manager, and Event:Add/Rem. Non-administrator user accounts can then access the Event Policy Manager page and disable one or more events on all devices. For more information on access hooks, see the section on Access Permissions.

To disable one or more events in the classic Skylar One user interface:

  1. Go to the Event Policy Manager page (Registry > Events > Event Manager).
  2. In the Event Policy Manager page, select the checkbox for each event you want to disable.
  3. In the Select Actions drop-down list, select DISABLE these Event Policies.
  4. Click the Go button. The selected event(s) no longer appear in Skylar One for any device, application, or policy.

Enabling an Event in the Classic User Interface

You can simultaneously disable one or more events on all devices. When an event is disabled, it no longer appears in the Event Console for any devices. You can also enable an event that has been disabled.

To enable an event on all devices, non-administrator user accounts must be granted one or more access keys that include the following access hooks: Registry, Registry>Events>Event Manager, and Event:Add/Rem. Non-administrator user accounts can then access the Event Policy Manager page and enable one or more events on all devices. For more information on access hooks, see the section on Access Permissions.

To enable one or more events in the classic Skylar One user interface:

  1. Go to the Event Policy Manager page (Registry > Events > Event Manager).
  2. In the Event Policy Manager page, select the checkbox for each event you want to enable.
  3. In the Select Actions drop-down list, select ENABLE these Event Policies.
  4. Click the Go button. The selected event(s) once again appear in Skylar One.